page 10 and 11 of <http://www.panduit.com/products/brochures/105309.pdf> says there's a way to move 20kW of heat away from a rack if your normal CRAC is moving 10kW (it depends on that basic air flow), permitting six blade servers in a rack. panduit licensed this tech from IBM a couple of years ago. i am intrigued by the possible drop in total energy cost per delivered kW, though in practice most datacenters can't get enough utility and backup power to run at this density. if "cooling doors" were to take off, we'd see data centers partitioned off and converted to cubicles. -- Paul Vixie
At 3:17 PM +0000 3/29/08, Paul Vixie wrote:
page 10 and 11 of <http://www.panduit.com/products/brochures/105309.pdf> says there's a way to move 20kW of heat away from a rack if your normal CRAC is moving 10kW (it depends on that basic air flow), permitting six blade servers in a rack. panduit licensed this tech from IBM a couple of years ago. i am intrigued by the possible drop in total energy cost per delivered kW, though in practice most datacenters can't get enough utility and backup power to run at this density.
While the chilled water door will provide higher equipment density per rack, it relies on water piping back to a "Cooling Distribution Unit" (CDU) which is in the corner sitting by your CRAC/CRAH units. Whether this is actually more efficient depends quite a bit on the (omitted) specifications for that unit... I know that it would have to be quite a bit before many folks would: 1) introduce another cooling system (with all the necessary redundancy), and 2) put pressurized water in the immediate vicinity of any computer equipment. /John
On Sat, 29 Mar 2008, John Curran wrote:
unit... I know that it would have to be quite a bit before many folks would: 1) introduce another cooling system (with all the necessary redundancy), and 2) put pressurized water in the immediate vicinity of any computer equipment.
What could possibly go wrong? :) If it leaks, you get the added benefits of conductive and evaporative cooling. ---------------------------------------------------------------------- Jon Lewis | I route Senior Network Engineer | therefore you are Atlantic Net | _________ http://www.lewis.org/~jlewis/pgp for PGP public key_________
jcurran@mail.com (John Curran) writes:
While the chilled water door will provide higher equipment density per rack, it relies on water piping back to a "Cooling Distribution Unit" (CDU) which is in the corner sitting by your CRAC/CRAH units.
it just has to sit near the chilled water that moves the heat to the roof. that usually means CRAC-adjacency but other arrangements are possible.
I know that it would have to be quite a bit before many folks would: 1) introduce another cooling system (with all the necessary redundancy), and 2) put pressurized water in the immediate vicinity of any computer equipment.
the pressure differential between the pipe and atmospheric isn't that much. nowhere near steam or hydraulic pressures. if it gave me ~1500w/SF in a dense urban neighborhood i'd want to learn more. -- Paul Vixie
At 7:06 PM +0000 3/29/08, Paul Vixie wrote:
While the chilled water door will provide higher equipment density per rack, it relies on water piping back to a "Cooling Distribution Unit" (CDU) which is in the corner sitting by your CRAC/CRAH units.
it just has to sit near the chilled water that moves the heat to the roof. that usually means CRAC-adjacency but other arrangements are possible.
When one of the many CRAC units decides to fail in an air-cooled environment, another one starts up and everything is fine. The nominal worse case leaves the failed CRAC unit as a potential air pressure leakage source for the raised-floor and/or ductwork, but that's about it. Chilled water to the rack implies multiple CDU's with a colorful hose and valve system within the computer room (effectively a miniature version of the facility chilled water loop). Trying to eliminate potential failure modes in that setup will be quite the adventure, which depending on your availability target may be a non-issue or a great reason to consider moving to new space. /John
John Curran wrote:
Chilled water to the rack implies multiple CDU's with a colorful hose and valve system within the computer room (effectively a miniature version of the facility chilled water loop). Trying to eliminate potential failure modes in that setup will be quite the adventure, which depending on your availability target may be a non-issue or a great reason to consider moving to new space.
Actually it wouldn't have to be pressurized at all if you located a large tank containing chilled water above and to the side, with a no-kink, straight line to the tank. N+1 chiller units could feed the tank. Thermo-siphoning would occur (though usually done with a cold line at the bottom and a return, warmed line at the top of the cooling device) as the warm water rises to the chilled tank and more chilled water flows down to the intake. You would of course have to figure out how to monitor/cut off/contain any leaks. Advantage is that cooling would continue up to the limit of the BTUs stored in the chilled water tank, even in the absence of power. Cordially Patrick Giagnocavo patrick@zill.net
On 29 Mar 2008, Paul Vixie wrote:
page 10 and 11 of <http://www.panduit.com/products/brochures/105309.pdf> says there's a way to move 20kW of heat away from a rack if your normal CRAC is moving 10kW (it depends on that basic air flow), permitting six blade servers in a rack. panduit licensed this tech from IBM a couple of years ago. i am intrigued by the possible drop in total energy cost per delivered kW, though in practice most datacenters can't get enough utility and backup power to run at this density. if "cooling doors" were to take off, we'd see data centers partitioned off and converted to cubicles.
Can someone please, pretty please with sugar on top, explain the point behind high power density? Raw real estate is cheap (basically, nearly free). Increasing power density per sqft will *not* decrease cost, beyond 100W/sqft, the real estate costs are a tiny portion of total cost. Moving enough air to cool 400 (or, in your case, 2000) watts per square foot is *hard*. I've started to recently price things as "cost per square amp". (That is, 1A power, conditioned, delivered to the customer rack and cooled). Space is really irrelevant - to me, as colo provider, whether I have 100A going into a single rack or 5 racks, is irrelevant. In fact, my *costs* (including real estate) are likely to be lower when the load is spread over 5 racks. Similarly, to a customer, all they care about is getting their gear online, and can care less whether it needs to be in 1 rack or in 5 racks. To rephrase vijay, "what is the problem being solved"? [not speaking as mlc anything]
Can someone please, pretty please with sugar on top, explain the point behind high power density?
maybe.
Raw real estate is cheap (basically, nearly free).
not in downtown palo alto. now, you could argue that downtown palo alto is a silly place for an internet exchange. or you could note that conditions giving rise to high and diverse longhaul and metro fiber density, also give rise to high real estate costs.
Increasing power density per sqft will *not* decrease cost, beyond 100W/sqft, the real estate costs are a tiny portion of total cost. Moving enough air to cool 400 (or, in your case, 2000) watts per square foot is *hard*.
if you do it the old way, which is like you said, moving air, that's always true. but, i'm not convinced that we're going to keep doing it the old way.
I've started to recently price things as "cost per square amp". (That is, 1A power, conditioned, delivered to the customer rack and cooled). Space is really irrelevant - to me, as colo provider, whether I have 100A going into a single rack or 5 racks, is irrelevant. In fact, my *costs* (including real estate) are likely to be lower when the load is spread over 5 racks. Similarly, to a customer, all they care about is getting their gear online, and can care less whether it needs to be in 1 rack or in 5 racks.
To rephrase vijay, "what is the problem being solved"?
if you find me 300Ksqft along the caltrain fiber corridor in the peninsula where i can get 10mW of power and have enough land around it for 10mW worth of genset, and the price per sqft is low enough that i can charge by the watt and floor space be damned and still come out even or ahead, then please do send me the address.
On Sat, Mar 29, 2008 at 06:54:02PM +0000, Paul Vixie wrote:
Can someone please, pretty please with sugar on top, explain the point behind high power density?
Customers are being sold blade servers on the basis that "it's much more efficient to put all your eggs in one basket" without being told about the power or cooling requirements and how not a whole lot of datacenters really want/are able to support customers installing 15 racks of blade servers in one spot with 4x 230V/30A circuits each. (Yes, I had that request.) Customers don't want to pay for the space. They forget that they still have to pay for the power and that that charge also includes a fee for the added load on the UPS as well as the AC to get rid of the heat. While there are advantages to blade servers, a fair number of sales are to gullable users who don't know what they're getting into, not those who really know how to get the most out of them. They get sold on the idea of using blade servers, stick them into S&D, Equinix, and others and suddenly find out that they can only fit 2 in a rack because of the per-rack wattage limit and end up having to buy the space anyway. (Wether it's extra racks or extra sq ft or meters, it's the same problem.) Under current rules for most 3rd party datacenters, one of the principle stated advantages, that of much greater density, is effectively canceled out.
Increasing power density per sqft will *not* decrease cost, beyond 100W/sqft, the real estate costs are a tiny portion of total cost. Moving enough air to cool 400 (or, in your case, 2000) watts per square foot is *hard*.
(Remind me to strap myself to the floor to keep from becoming airborne by the hurricane force winds while I'm working in your datacenter.) Not convinved of the first point but experience is limited there. For the second, I think the practical upper bound for my purposes is probably between 150 and 200 watts per sq foot. (Getting much harder once you cross the 150 watt mark.) Beyond that, it gets quite difficult to supply enough cool air to the cabinet to keep the equipment happy unless you can guarentee a static load and custom design for that specific load. (And we all know that will never happen.) And don't even talk to me about enclosed cabinets at that point.
if you do it the old way, which is like you said, moving air, that's always true. but, i'm not convinced that we're going to keep doing it the old way.
One thing I've learned over the various succession of datacenter / computer room builds and expansions that I've been involved in is that if you ask the same engineer about the right way to do cooling in medium and large scale datacenters (15k sq ft and up), you'll probably get a different oppinion every time you ask the question. There are several theories of how best to hand this and *none* of them are right. No one has figured out an ideal solution and I'm not convinced an ideal solution exists. So we go with what we know works. As people experiment, what works changes. The problem is that retrofitting is a bear. (When's the last time you were able to get a $350k PO approved to update cooling to the datacenter? If you can't show a direct ROI, the money people don't like you. And on a more practical line, how many datacenters have you seen where it is physically impossible to remove the CRAC equipment for replacement without first tearing out entire rows of racks or even building walls?) Anyway, my thoughts on the matter. -Wayne --- Wayne Bouchard web@typo.org Network Dude http://www.typo.org/~web/
Can someone please, pretty please with sugar on top, explain the point behind high power density?
It allows you to market your operation as a "data center". If you spread it out to reduce power density, then the logical conclusion is to use multiple physical locations. At that point you are no longer centralized. In any case, a lot of people are now questioning the traditional data center model from various angles. The time is ripe for a paradigm change. My theory is that the new paradigm will be centrally managed, because there is only so much expertise to go around. But the racks will be physically distributed, in virtually every office building, because some things need to be close to local users. The high speed fibre in Metro Area Networks will tie it all together with the result that for many applications, it won't matter where the servers are. Note that the Google MapReduce, Amazon EC2, Haddoop trend will make it much easier to place an application without worrying about the exact locations of the physical servers. Back in the old days, small ISPs set up PoPs by finding a closet in the back room of a local store to set up modem banks. In the 21st century folks will be looking for corporate data centers with room for a rack or two of multicore CPUs running XEN, and Opensolaris SANs running ZFS/raidz providing iSCSI targets to the XEN VMs. --Michael Dillon
On 3/29/08, Alex Pilosov <alex@pilosoft.com> wrote:
Can someone please, pretty please with sugar on top, explain the point behind high power density?
Raw real estate is cheap (basically, nearly free). Increasing power density per sqft will *not* decrease cost, beyond 100W/sqft, the real estate costs are a tiny portion of total cost. Moving enough air to cool 400 (or, in your case, 2000) watts per square foot is *hard*.
I've started to recently price things as "cost per square amp". (That is, 1A power, conditioned, delivered to the customer rack and cooled). Space is really irrelevant - to me, as colo provider, whether I have 100A going into a single rack or 5 racks, is irrelevant. In fact, my *costs* (including real estate) are likely to be lower when the load is spread over 5 racks. Similarly, to a customer, all they care about is getting their gear online, and can care less whether it needs to be in 1 rack or in 5 racks.
To rephrase vijay, "what is the problem being solved"?
I have not yet found a way to split the ~10kw power/cooling demand of a T1600 across 5 racks. Yes, when I want to put a pair of them into an exchange point, I can lease 10 racks, put T1600s in two of them, and leave the other 8 empty; but that hasn't helped either me the customer or the exchange point provider; they've had to burn more real estate for empty racks that can never be filled, I'm paying for floor space in my cage that I'm probably going to end up using for storage rather than just have it go to waste, and we still have the problem of two very hot spots that need relatively 'point' cooling solutions. There are very specific cases where high density power and cooling cannot simply be spread out over more space; thus, research into areas like this is still very valuable. Matt
Matthew Petach wrote:
On 3/29/08, Alex Pilosov <alex@pilosoft.com> wrote:
Can someone please, pretty please with sugar on top, explain the point behind high power density?
Raw real estate is cheap (basically, nearly free). Increasing power density per sqft will *not* decrease cost, beyond 100W/sqft, the real estate costs are a tiny portion of total cost. Moving enough air to cool 400 (or, in your case, 2000) watts per square foot is *hard*.
I've started to recently price things as "cost per square amp". (That is, 1A power, conditioned, delivered to the customer rack and cooled). Space is really irrelevant - to me, as colo provider, whether I have 100A going into a single rack or 5 racks, is irrelevant. In fact, my *costs* (including real estate) are likely to be lower when the load is spread over 5 racks. Similarly, to a customer, all they care about is getting their gear online, and can care less whether it needs to be in 1 rack or in 5 racks.
To rephrase vijay, "what is the problem being solved"?
I have not yet found a way to split the ~10kw power/cooling demand of a T1600 across 5 racks. Yes, when I want to put a pair of them into an exchange point, I can lease 10 racks, put T1600s in two of them, and leave the other 8 empty; but that hasn't helped either me the customer or the exchange point provider; they've had to burn more real estate for empty racks that can never be filled, I'm paying for floor space in my cage that I'm probably going to end up using for storage rather than just have it go to waste, and we still have the problem of two very hot spots that need relatively 'point' cooling solutions.
There are very specific cases where high density power and cooling cannot simply be spread out over more space; thus, research into areas like this is still very valuable.
The problem with "point" heating is often that the hot point is then the *intake* for other equipment. If you spread your two T1600s into 10 racks (i.e. skip 2, drop one, skip 4, drop 1, leaving two at the end) your hot point problem is much less of a concern. If you bought 10 racks... not in a row, but SURROUNDING (in each of the rows opposite the cabinets)... Say 12 (a = vacant, b,c = T1600) aaaa abca aaaa You would be doing everyone in your datacenter a service by a) not thinking linearly and b) providing adequate sq ft space to dissipate your heat. Deepak