Good job. I've had to deal with assorted water problems, thankfully not recently. Some lessons were learned. These water problems were indirectly or directly caused by firefighting. 1. When the data/comm center is on a bottom floor, consider floor drains at the time of installation. Might want emergency access to pumps, or even wet-dry shop vacs. 2. We had a repeated problem in several moderate-rise buildings where there were fairly frequent, although small, fires on upper floors. Water, of course, runs downhill. Some things done (this was the US Senate offsite computer center) a. Put waterproof gaskets on the emergency stairs that had entrances from the control room. b. When it happened often enough, we mounted rolled-up plastic tarps on rollers suspended from the ceiling, with a good solid handle dangling down on a rope. During the peak problem period, we'd hear an alarm, pull the tarps over the equipment, and then do a fast power-down (not necessarily emergency pull--this depended on heat buildup). The tarps were a few inches over the top of the racks, to leave some room for emergency airflow during cooldown. 3. Consider putting data centers not in the ground floor on the basement, but not too high either. Sean, I believe, knows the specific NFPA rule, but IIRC you can't have a UPS with acid electrolyte above the third floor. So, you can put a data center on the 2nd floor and both allow the UPS and have a place for the water to drain.
On Sun, Oct 20, 2002 at 01:22:50PM -0400, Howard C. Berkowitz wrote:
I've had to deal with assorted water problems, thankfully not recently. Some lessons were learned. These water problems were indirectly or directly caused by firefighting.
1. When the data/comm center is on a bottom floor, consider floor drains at the time of installation. Might want emergency access to pumps, or even wet-dry shop vacs.
Corrolary: If your data center is on the ground floor or in the basement, remember that the sump pump must be on a UPS/generator protected circuit. Not that I learned this one the hard way or anything. *cough* -P.
At 2:03 PM -0400 10/19/02, Sean Donelan wrote:
Stuff happens to everyone, its how you respond. Would your company have been able to recover as quickly?
Over one weekend I was part of a team of folks involved in moving a voice/data center for a fairly sizeable regional office across the city in Atlanta. We had pretty much everything moved, installed and working by Saturday night. Early Sunday morning as we were tidying up, someone called over the portable radios that it was 'raining in the data center!' If I remember correctly, it was a return pipe for the cooling system had come apart at a poorly soldered connection in the ceiling above the UPS. Soon enough a good portion of the floor tiles came down and the underneath the raised floor a nice pond was forming. Since it was a Sunday morning, it took some time before some building engineers could be called in to turn off building water. By that time, the 1' raised floor was pretty well full. We were on an upper floor, maybe 7 or so. I don't remember actual amount of water, but there was water draining into the third level deep parking garage below. Some servers had been permanantly damaged, but most equipment including some servers (remember NetFRAMEs?), hubs, routers, the cabling system and a PBX survived to provide service until the insurance company provided funds for everything to be replaced. Having good vendor relationships helped significantly in my experience. Many were overnighting equipment without requiring a lot of red tape. Having access to a bunch of hair dryers was also useful. :-) John