Re: Looking for advice on datacenter electrical/generator

Just to give a working example, we currently have 2 redundant UPS's that typically will have over an hour runtime each (at current load) and an estimated 10 minute runtime each under a full load. Our generator and genset have us up on alternate power in approximately 10 seconds barring any odd problems with the generator, but a weekly exercise would typically identify a problem like this which can hopefully be corrected prior to needing the generator. A manual override of the transfer switch is possible if a failure should ever occur in that as well. HVAC is powered by the generator when it's running but not by UPS because of the tremendous draw it would have on the UPS's shortening battery runtime. 4 HVAC units usually keep it pretty cool, around or 60 degrees Fahrenheit so 10 seconds of all of them being off is not a problem. Even 10 minutes wouldn't raise the temperature all that much where it couldn't be cooled down rapidly when power is back online. Our currently fuel capacity (at current load) will allow us to run off generator for a few weeks without refueling. I'm sure this is all pretty standard for most people with similar setups. Hope this helps! At 03:37 PM 4/2/2003 -0800, you wrote:
Vinny Abello Network Engineer Server Management vinny@tellurian.com (973)300-9211 x 125 (973)940-6125 (Direct) PGP Key Fingerprint: 3BC5 9A48 FC78 03D3 82E0 E935 5325 FBCB 0100 977A Tellurian Networks - The Ultimate Internet Connection http://www.tellurian.com (888)TELLURIAN There are 10 kinds of people in the world. Those who understand binary and those that don't.