UPS failure modes (was: fire at NAC)
At 12:27 AM 5/29/2003 -0400, you wrote:
Sheesh. Heh.
We're still here.
Part of a rectifier in a Liebert UPS let loose, causing a momentary fire. That is, until the FM200 quenched it.
Since there seems to be interest, I will post the post-mortem to the list.
I had a little 2000VA rackmount Liebert UPS catch fire in 1997 and another new and improved Liebert model almost catch fire about a year later. Both were operating well within specified input, load, and temperature parameters. I haven't really trusted them since.I bought dual MGE UPSes for our datacenter in 2002. I figured if E****s can flip them on and off randomly and massively overload them all in an environment which is 95 degrees F, then they should hold up nicely for us when lightly loaded at 65 degrees F. :) The reason for this rambling post is to ask if others have had similar problems with other UPS brands. I think they should have enough fail-safes built-in that they are never the CAUSE of an outage much less a fire! Based on my experience and NAC's incident today, is that an unreasonable expectation? I don't think manufacturers specify MTBF (mean time before fire) figures for UPS units. What have others experienced as the failure mode(s) for their UPS(s)? The static transfer switch should drop the load onto line/bypass power immediately and shut down the inverter while tripping the battery disconnect at the first sign of trouble - does this work as designed and advertised most of the time or just some of the time? Of those with UPS failure histories, what has happened in your situation? Robert Tellurian Networks - The Ultimate Internet Connection http://www.tellurian.com | 888-TELLURIAN | 973-300-9211 "Good will, like a good name, is got by many actions, and lost by one." - Francis Jeffrey
> I had a little 2000VA rackmount Liebert UPS catch fire in 1997 and another > new and improved Liebert model almost catch fire about a year later. > What have others experienced as the failure mode(s) for their > UPS(s)? We had a two-hour grid power outage here in Berkeley yesterday, during which time our APC Symmetra 16kva fried two of its four batteries, and went into bypass mode, which meant that the transition back from generator to grid caused everything to reboot. :-/ I've seen two previous APCs (both Matrixes) fry batteries... The batteries balloon up, and get really hot, and are too big to extract from the chassis. APC's solution to this is to have us take the entire UPS offline for several days to completely dissipate the heat, and then try to force the batteries out. Since this seems to be an endemic problem, you'd think they'd just design a chassis with somewhat more clearance around the batteries so that failed ones could still be physically extracted. -Bill
I've seen two previous APCs (both Matrixes) fry batteries... The batteries balloon up, and get really hot, and are too big to extract from the chassis. APC's solution to this is to have us take the entire UPS offline for several days to completely dissipate the heat, and then try to
I've got a few APC SmartUPS's in the shop at home that I disassembled last week. Two SU1400's and one much older SU 2000. All of them had overheated and exploded cells. The 1400's all leaked and were /very/ wedged in. I ended up removing the outer shell, then the circuit board. Once these were out of the way they frame spread enough to allow the swollen casings to slide out. Both of these had acid all over the bottoms. One of these had been leaking so long that it ate a ~1/4 inch hole through the bottom. The 2000 had the worst batteries, but once I got the plastic battery casing opened (I CAN see why they stopped using this design...) and got all of the connections apart, the cells just dumped right out. Maybe I'll take some pictures of the batterys...it was sort of fun to see how they had expanded and wrapped around each other. :) I've only heard one report of APC's that caught fire...and even then it was just the carpet below that caught fire. ...david --- david raistrick drais@atlasta.net http://www.expita.com/nomime.html
On Thu, 29 May 2003, Bill Woodcock wrote:
I've seen two previous APCs (both Matrixes) fry batteries... The batteries balloon up, and get really hot, and are too big to extract from the chassis.
I've also personally witnessed an APC do this. I'm not a fan of APC. They sent us a replacement APC but I still prefer the rack mount Tripp Lites we used at the last company I worked for. Gerald
On Thu, 29 May 2003, Gerald wrote:
On Thu, 29 May 2003, Bill Woodcock wrote:
I've seen two previous APCs (both Matrixes) fry batteries... The batteries balloon up, and get really hot, and are too big to extract from the chassis. I've also personally witnessed an APC do this. I'm not a fan of APC. They sent us a replacement APC but I still prefer the rack mount Tripp Lites we used at the last company I worked for.
Anyone had experience with Belkin UPSes? Theyre much cheaper than APC, and seem to have a longer runtime. I wonder about the long term reliability though. Data points would be helpful. -Dan -- [-] Omae no subete no kichi wa ore no mono da. [-]
On Thu, 29 May 2003, Dan Hollis wrote:
On Thu, 29 May 2003, Gerald wrote:
On Thu, 29 May 2003, Bill Woodcock wrote:
I've seen two previous APCs (both Matrixes) fry batteries... The batteries balloon up, and get really hot, and are too big to extract from the chassis. I've also personally witnessed an APC do this. I'm not a fan of APC. They sent us a replacement APC but I still prefer the rack mount Tripp Lites we used at the last company I worked for.
Anyone had experience with Belkin UPSes? Theyre much cheaper than APC, and seem to have a longer runtime. I wonder about the long term reliability though. Data points would be helpful.
We were all set to buy a dozen APC 750s, a half dozen or so APC 1400s, and another hald dozen APC 2200s a year or so ago. We had approval for the purchase from the director and provided the exact model numbers and quantities to our purchasing officer. Our purchasing officer came back sometime later and suggested we purchase Minuteman UPSs because they were on sale at the time. We never did get to purchase any UPSs. grr... That said, Minuteman's Entreprise UPS series looks to be pretty good. Does anyone have any experience with them? We were planning on buying large 2x00VA UPSs to handle Enterasys 6000 chassis (pl). Justin
(header trimmed) Hello, First off, we're all still alive here. Underlying root cause was a failure of a capacitor in the rectifier section. We're not sure what actually caused the failure of the failure of the capacitor, but it resulted in the internals of the capacitor being ejected from the UPS at such a high rate of speed, that it dented the front door of the UPS itself, and caused the door to jump the lock and swing open. I, personally, have never been a fan of Liebert UPS's. The electrical engineer that we use seems to share my assessment that Lieberts, at least Series 300's, are not built as well as the could be. I have no direct experience with MGE, but I recall several multi-hour outages in Jersey City Exodus, that I think had something to do with MGE systems. I don't recall if that was human error, or not. Another negative there, for me, is that they are French. We own about 8 or so Matrix 5000's; out of box failure rate is hovering at about 50%, and failure rate within first month of operation is about 75%. However, once they pass that barrier, they tend to work. Don't overload them, they tend to get cranky. We had one shoot flames, once, but that wasn't assosciated with an overload. My personal favorite: Exide/Powerware/Invensys 9315's. They just work. I have two of them, an 80 and a 500. The 80 has been installed for nearly 4 years, and has never, ever dropped the critical load unless instructed to. The 500 is a recent install, but seems to be doing just fine as well.
From folks I've talked to (engineers and industry people), Powerware seems to be known as the UPS that just works. I've yet to talk to one person who had a powerware die on them. Myself included.
On Thu, 29 May 2003, Dan Hollis wrote:
On Thu, 29 May 2003, Gerald wrote:
On Thu, 29 May 2003, Bill Woodcock wrote:
I've seen two previous APCs (both Matrixes) fry batteries... The batteries balloon up, and get really hot, and are too big to extract from the chassis. I've also personally witnessed an APC do this. I'm not a fan of APC. They sent us a replacement APC but I still prefer the rack mount Tripp Lites we used at the last company I worked for.
Anyone had experience with Belkin UPSes? Theyre much cheaper than APC, and seem to have a longer runtime. I wonder about the long term reliability though. Data points would be helpful.
-Dan -- [-] Omae no subete no kichi wa ore no mono da. [-]
-- Alex Rubenstein, AR97, K2AHR, alex@nac.net, latency, Al Reuben -- -- Net Access Corporation, 800-NET-ME-36, http://www.nac.net --
On Thu May 29, 2003 at 04:29:13PM -0400, Alex Rubenstein wrote:
From folks I've talked to (engineers and industry people), Powerware seems to be known as the UPS that just works. I've yet to talk to one person who had a powerware die on them. Myself included.
We are a Powerware house. We had a large number of 3kVA and 6kVA units in our previous data centre (no-one would stump up the cash for a large unit so we had to buy them as we needed them). After about 5 years (very rough figure), we've now had 3 or 4 units fail, sometimes in the UPS, sometimes in the bypass unit. They all seem to be component failures (in the case of the bypass unit, a leg broke off a small capacitor). I don't think we've replaced any of the batteries in that time and they're still all holding charge well, even at full load. At our new site we have some 50kVA and 80kVA units that we inherited from the previous owners. One is already exhibiting the signs of a failing fan, but we have no idea what their history is before we moved in. Simon -- Simon Lockhart | Tel: +44 (0)1628 407720 (x37720) | Si fractum Technology Manager | Fax: +44 (0)1628 407701 (x37701) | non sit, noli BBC Internet Services | Email: Simon.Lockhart@bbc.co.uk | id reficere BBC Technology, Maiden House, Vanwall Road, Maidenhead. SL6 4UB. UK
On Thu, 29 May 2003, Simon Lockhart wrote:
On Thu May 29, 2003 at 04:29:13PM -0400, Alex Rubenstein wrote:
From folks I've talked to (engineers and industry people), Powerware seems to be known as the UPS that just works. I've yet to talk to one person who had a powerware die on them. Myself included.
We are a Powerware house. We had a large number of 3kVA and 6kVA units in our previous data centre (no-one would stump up the cash for a large unit so we had to buy them as we needed them). After about 5 years (very rough figure), we've now had 3 or 4 units fail, sometimes in the UPS, sometimes in the bypass unit. They all seem to be component failures (in the case of the bypass unit, a leg broke off a small capacitor). I don't think we've replaced any of the batteries in that time and they're still all holding charge well, even at full load.
Perhaps I should have been clear. In my entire post, sed s/powerware/powerware 9315/g
At our new site we have some 50kVA and 80kVA units that we inherited from the previous owners. One is already exhibiting the signs of a failing fan, but we have no idea what their history is before we moved in.
Well, fans would fall under maintenance, no? Perhaps, also, someone is not changing filters, or whatnot. -- Alex Rubenstein, AR97, K2AHR, alex@nac.net, latency, Al Reuben -- -- Net Access Corporation, 800-NET-ME-36, http://www.nac.net --
We are a Powerware house. We had a large number of 3kVA and 6kVA units in our previous data centre (no-one would stump up the cash for a large unit so we had to buy them as we needed them). After about 5 years (very rough figure), we've now had 3 or 4 units fail, sometimes in the UPS, sometimes in the bypass unit. They all seem to be component failures (in the case of the bypass unit, a leg broke off a small capacitor). I don't think we've replaced any of the batteries in that time and they're still all holding charge well, even at full load.
Several data centers at which I have been involved in the maintenance of have used Powerware UPSes. We've had great luck with them everywhere i've been, and this includes service and support. The service I have received from them (at least in the Southeast US) has been nothing short of phenomenal, including calls from the reps years after they were purchased, even on small installations, with promises made and kept time and time again. I have never been disappointed. I'd like to echo the results of other posters: We replaced Liebert with Powerware in two or three of those installations and had great luck, where the Liebert units would come out with spotty failures on a fairly regular basis (components, etc). Personally, i'd like to hear from more people who are doing serious work with DC power in a collocation environment (with the market reality of customers who want AC). I have seen customers request DC and nothing but. Tim
On Thu, May 29, 2003 at 04:29:13PM -0400, Alex Rubenstein wrote:
I have no direct experience with MGE, but I recall several multi-hour outages in Jersey City Exodus, that I think had something to do with MGE
Correct. There were, if I recall correctly, a total of five in a short period, including two in one night. To be fair, the second of those was human error, the result of aggressive management pushing hard against engineering recommendations at three in the morning when folks were already hyped up on adrenaline and lack of sleep from the first. That was when Exodus lost my business forever.
systems. I don't recall if that was human error, or not. Another negative there, for me, is that they are French.
*snicker* -Pete
On Thu, 29 May 2003, Bill Woodcock wrote:
> I had a little 2000VA rackmount Liebert UPS catch fire in 1997 and another > new and improved Liebert model almost catch fire about a year later. > What have others experienced as the failure mode(s) for their > UPS(s)?
We had a two-hour grid power outage here in Berkeley yesterday, during which time our APC Symmetra 16kva fried two of its four batteries, and went into bypass mode, which meant that the transition back from generator to grid caused everything to reboot. :-/
I've seen two previous APCs (both Matrixes) fry batteries... The batteries balloon up, and get really hot, and are too big to extract from the chassis. APC's solution to this is to have us take the entire UPS offline for several days to completely dissipate the heat, and then try to force the batteries out. Since this seems to be an endemic problem, you'd think they'd just design a chassis with somewhat more clearance around the batteries so that failed ones could still be physically extracted.
gell cells suffer from an electron mobility problem relative to traditional lead acid batteries. If you pull to much current off a stack of them you can boil the electrolyte off in a very big hurry, but because they're sealed they'll distent before they explode instead of just venting. I have run a matrix 5000xr with 4 battery enclosures down to zero under 65% load (220 minutes) without any untoward effects. in 100% load or overload conditions without forced air cooling (we lose ours in power outages) things could get uncomfortably warm.
-Bill
-- -------------------------------------------------------------------------- Joel Jaeggli Academic User Services joelja@darkwing.uoregon.edu -- PGP Key Fingerprint: 1DE9 8FCA 51FB 4195 B42A 9C32 A30D 121E -- In Dr. Johnson's famous dictionary patriotism is defined as the last resort of the scoundrel. With all due respect to an enlightened but inferior lexicographer I beg to submit that it is the first. -- Ambrose Bierce, "The Devil's Dictionary"
We are opening a new facility in SF and are seriously considering the idea of by passing a large UPS (150-225KVA)altogether and relay on a generator 400-450KW with small UPSes on each rack. A UPS failure would be limited to a single rack, this way we could My personal experience with ATSes is limited and would appreciate any feedback. Our new facility is dual feed from two different power grids and we could provide two independant power feeds to each rack one backed via a generator and the other std house power. Customer are welcome to bring their own UPS. (we know it takes away rack space). FYI; Our experience has shown that all UPSes (we have used APC, Best, Liebert and Minute Man) have all failed within a 5 year period. We have over 30 APC UPSes and a ~20% failure rate. thanks arman Joel Jaeggli wrote:
On Thu, 29 May 2003, Bill Woodcock wrote:
> I had a little 2000VA rackmount Liebert UPS catch fire in 1997 and another > new and improved Liebert model almost catch fire about a year later. > What have others experienced as the failure mode(s) for their > UPS(s)?
We had a two-hour grid power outage here in Berkeley yesterday, during which time our APC Symmetra 16kva fried two of its four batteries, and went into bypass mode, which meant that the transition back from generator to grid caused everything to reboot. :-/
I've seen two previous APCs (both Matrixes) fry batteries... The batteries balloon up, and get really hot, and are too big to extract from the chassis. APC's solution to this is to have us take the entire UPS offline for several days to completely dissipate the heat, and then try to force the batteries out. Since this seems to be an endemic problem, you'd think they'd just design a chassis with somewhat more clearance around the batteries so that failed ones could still be physically extracted.
gell cells suffer from an electron mobility problem relative to traditional lead acid batteries. If you pull to much current off a stack of them you can boil the electrolyte off in a very big hurry, but because they're sealed they'll distent before they explode instead of just venting.
I have run a matrix 5000xr with 4 battery enclosures down to zero under 65% load (220 minutes) without any untoward effects. in 100% load or overload conditions without forced air cooling (we lose ours in power outages) things could get uncomfortably warm.
-Bill
-- -------------------------------------------------------------------------- Joel Jaeggli Academic User Services joelja@darkwing.uoregon.edu -- PGP Key Fingerprint: 1DE9 8FCA 51FB 4195 B42A 9C32 A30D 121E -- In Dr. Johnson's famous dictionary patriotism is defined as the last resort of the scoundrel. With all due respect to an enlightened but inferior lexicographer I beg to submit that it is the first. -- Ambrose Bierce, "The Devil's Dictionary"
Arman wrote:
We are opening a new facility in SF and are seriously considering the idea of by passing a large UPS (150-225KVA)altogether and relay on a generator 400-450KW with small UPSes on each rack. A UPS failure would be limited to a single rack, this way we could
We run a configuration similar to this, except we do failure per-row with one APC Symmetra supporting between 3 and 6 cabinets, depending on the projected load. In the past 2.5(?) years, we've had one controller failure that did not cause an outage. All the batteries are fine, though we have not run them to zero. It turned out to be a very clean install as far as conduit and cabling goes, we're very happy with it. -- nicholas harteau nrh@ikami.com
nicholas harteau wrote:
We run a configuration similar to this, except we do failure per-row with one APC Symmetra supporting between 3 and 6 cabinets, depending on the projected load. In the past 2.5(?) years, we've had one controller failure that did not cause an outage. All the batteries are fine, though we have not run them to zero. It turned out to be a very clean install as far as conduit and cabling goes, we're very happy with it.
We do the same for one of our data centers, except we borrow one of the telco generator trucks due to lack of facility for an onsite generator. We have it setup to power both our Symmetra's as well as the telco's battery array one floor up. We've replaced two batteries and one powersupply in about 4 years (all recent) and had the Symmetra panic and warm reboot when electricity was being rerouted once. The warm reboot was interesting. It reboot every APC MasterSwitch and 90% of our routers. 10% of our routers and all servers stayed live even though their MasterSwitch's reloaded firmware. Go figure. I wouldn't have minded except that the Cat had been up for over 3 years without a reboot and I really wanted someone onsite when that took place. :) -Jack
On Thu, 2003-05-29 at 18:31, Robert Boyle wrote:
I had a little 2000VA rackmount Liebert UPS catch fire in 1997 and another new and improved Liebert model almost catch fire about a year later. Both were operating well within specified input, load, and temperature parameters. I haven't really trusted them since.I bought dual MGE UPSes for our datacenter in 2002. I figured if E****s can flip them on and off randomly and massively overload them all in an environment which is 95 degrees F, then they should hold up nicely for us when lightly loaded at 65 degrees F. :)
I am personally of the opposite opinion, we have never had any issues with our Liebert UPS'es, however we have had a few MGE's blow up. I can't comment on their small UPS models though, I think the smallest MGE or Liebert we have is 10KVA. The worst of the cases was an installation where we had dual 40KVA MGE UPS'es installed, both of whom failed critically within 48 hours of each other. Despite all the fail-safe circuitry they were bought with, they failed HARD (and yes, they had sparks and smoke coming out of them), and not even the bypass features worked. Since the second failed before the first one had been completely restored (it was being investigated to find the root cause of this critical failure), things went very black, and electricians had a pretty hectic time as they had to manually bypass the UPS'es completely and feed grid power directly to the facility. Unfortunately these two were bought at the same time (and came from the same production batch), so they had the same fault - which was apparently a bad shipment of capacitors which started to leak fluid after a period of time. Due to some unfortunate design choices in the MGE's, these capacitors happened to be placed directly above the main controller circuitry, and the leaky capacitors eventually caused the whole thing to short, in a rather spectacular way I might add. And yes, the bypass failed as well, we were explained the reason for this by the engineers from MGE although I can't say I remember the details (electricity really isn't my field :). That being said, after the replacement of the fried components, the engineers from MGE came on-site and rebuilt the entire bypass system in these two boxes some time later, at no charge of course - and we have not had any problems with them in the two years they have now been in operation after this incident. /leg
On Thu, 29 May 2003, Robert Boyle wrote:
The reason for this rambling post is to ask if others have had similar problems with other UPS brands. I think they should have enough fail-safes built-in that they are never the CAUSE of an outage much less a fire! Based on my experience and NAC's incident today, is that an unreasonable expectation? I don't think manufacturers specify MTBF (mean time before
A quote from the facility manager of a large ISP with multiple data centers in Northern Virginia, each using a different brand of UPS and backup systems (batteries, flywheels, generators, etc). Q: Which UPS brand do you think is best? A: They all suck! UPSes (and UPS batteries) do fail, sometimes in catastrophic ways. I would not design any critical system on the assumption that any particular component won't fail. High availability is about designing for failure. Sometimes there is a long time between failures, other times they occur early and often. The most annoying thing about UPSes is they fail at exactly the time they are needed most. The FCC NRIC Focus Group 2 is now accepting "voluntary" outage reports from Internet Service Providers. See http://www.nric.org/ for details.
UPSes (and UPS batteries) do fail, sometimes in catastrophic ways. I would not design any critical system on the assumption that any particular component won't fail. High availability is about designing for failure. Sometimes there is a long time between failures, other times they occur early and often. The most annoying thing about UPSes is they fail at exactly the time they are needed most.
Except, that: Even in instances where 'High availability' is designed, in the case where one of the units has a failure that causes a fire and FM200 dump, either the FM200 will still trigger an EPO, or the fire department will. So, the second 'high available' unit will generally not prevent you from dropping the critical load, but instead, will help you get back on line quicker. A much cheaper and easier to implement external maintenance make-before-break bypass will accomplish the same thing. I've heard many a story of the paralleling gear causing the problem in the first place, as well... -- Alex Rubenstein, AR97, K2AHR, alex@nac.net, latency, Al Reuben -- -- Net Access Corporation, 800-NET-ME-36, http://www.nac.net --
Or we could all take a page from the book of telecom, and run with DC systems. No inverters involved, lots of parallel rectifiers and battery power just sitting there. If only the equipment manufacturers would stop gauging on price for DC equipment/power supplies. Dan. Alex Rubenstein wrote:
UPSes (and UPS batteries) do fail, sometimes in catastrophic ways. I would not design any critical system on the assumption that any particular component won't fail. High availability is about designing for failure. Sometimes there is a long time between failures, other times they occur early and often. The most annoying thing about UPSes is they fail at exactly the time they are needed most.
Except, that:
Even in instances where 'High availability' is designed, in the case where one of the units has a failure that causes a fire and FM200 dump, either the FM200 will still trigger an EPO, or the fire department will.
So, the second 'high available' unit will generally not prevent you from dropping the critical load, but instead, will help you get back on line quicker.
A much cheaper and easier to implement external maintenance make-before-break bypass will accomplish the same thing.
I've heard many a story of the paralleling gear causing the problem in the first place, as well...
-- Alex Rubenstein, AR97, K2AHR, alex@nac.net, latency, Al Reuben -- -- Net Access Corporation, 800-NET-ME-36, http://www.nac.net --
On Thu, 29 May 2003, Alex Rubenstein wrote:
Even in instances where 'High availability' is designed, in the case where one of the units has a failure that causes a fire and FM200 dump, either the FM200 will still trigger an EPO, or the fire department will.
Why do you think most telephone central offices don't have EPO's? It is possible to meet code without an EPO, if you have a smart PE on the project.
So, the second 'high available' unit will generally not prevent you from dropping the critical load, but instead, will help you get back on line quicker.
That's why you have geographic diversity, if one node goes down the other location may be unaffected.
A much cheaper and easier to implement external maintenance make-before-break bypass will accomplish the same thing.
Pick two out of three. The "Internet philosphy" has tended to be a lots of cheap equipment connected by diverse paths. Designing for failure also means defining "failure" in terms of the service, not particular pieces of equipment. I don't care how many 9's your switch is, I just care if my packets get through.
I've heard many a story of the paralleling gear causing the problem in the first place, as well...
Yep, tieing together "redundant" systems with parelleling gears turns two independent systems into one "co-dependent" system. In a failure situation, you want to compartmentalize the failure. Loosing half your systems may be better than loosing all your systems.
SD> Date: Thu, 29 May 2003 16:53:43 -0400 (EDT) SD> From: Sean Donelan SD> Yep, tieing together "redundant" systems with parelleling SD> gears turns two independent systems into one "co-dependent" SD> system. In a failure situation, you want to compartmentalize SD> the failure. Loosing half your systems may be better than SD> loosing all your systems. Too bad a substantial amount of equipment doesn't allow for redundant plugins. The ability to plug { servers | routers | whatever } into two totally separate power feeds is nice. Anyone for building a rackmount transfer switch for two inputs? Assuming it didn't fail (!) -- would the economies of scale work for or against it compared to big transfer switches? Between dealing with _much_ smaller current levels and the opportunity for mass production, what are the chances of something like this working? Eddy -- Brotsman & Dreger, Inc. - EverQuick Internet Division Bandwidth, consulting, e-commerce, hosting, and network building Phone: +1 (785) 865-5885 Lawrence and [inter]national Phone: +1 (316) 794-8922 Wichita ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Date: Mon, 21 May 2001 11:23:58 +0000 (GMT) From: A Trap <blacklist@brics.com> To: blacklist@brics.com Subject: Please ignore this portion of my mail signature. These last few lines are a trap for address-harvesting spambots. Do NOT send mail to <blacklist@brics.com>, or you are likely to be blocked.
On Thu, 29 May 2003, Sean Donelan wrote:
UPSes (and UPS batteries) do fail, sometimes in catastrophic ways. I would not design any critical system on the assumption that any particular component won't fail. High availability is about designing for failure. Sometimes there is a long time between failures, other times they occur early and often. The most annoying thing about UPSes is they fail at exactly the time they are needed most.
ok, what UPSes do telcos use (besides their monster battery arrays) -Dan -- [-] Omae no subete no kichi wa ore no mono da. [-]
On Thu, 29 May 2003, Jack Bates wrote:
Dan Hollis wrote:
ok, what UPSes do telcos use (besides their monster battery arrays) What's wrong with our monster battery arrays?
They dont tend to fit in 19" rackmounts -Dan -- [-] Omae no subete no kichi wa ore no mono da. [-]
Thus spake "Dan Hollis" <goemon@anime.net>
On Thu, 29 May 2003, Jack Bates wrote:
Dan Hollis wrote:
ok, what UPSes do telcos use (besides their monster battery arrays) What's wrong with our monster battery arrays?
They dont tend to fit in 19" rackmounts
You wouldn't mount a "monster array" in 19" racks anyways. Telco battery strings often take up entire floors, or at least significant portions of them, and per building codes have to be enclosed (e.g. basement) to contain fumes, leaks, or explosions. Things get a bit more complicated safety-wise when you're talking 24-48 hours of capacity. S Stephen Sprunk "God does not play dice." --Albert Einstein CCIE #3723 "God is an inveterate gambler, and He throws the K5SSS dice at every possible opportunity." --Stephen Hawking
On Thu, 29 May 2003, Stephen Sprunk wrote:
Thus spake "Dan Hollis" <goemon@anime.net>
On Thu, 29 May 2003, Jack Bates wrote:
Dan Hollis wrote:
ok, what UPSes do telcos use (besides their monster battery arrays) What's wrong with our monster battery arrays? They dont tend to fit in 19" rackmounts You wouldn't mount a "monster array" in 19" racks anyways.
Yes, I was specifically asking what telcos use when they dont use the battery arrays. Eg what do they use in remote cabinets or customer premise sites... I thought it was a simple question, guess not. -Dan -- [-] Omae no subete no kichi wa ore no mono da. [-]
On Fri, 30 May 2003, Dan Hollis wrote:
On Thu, 29 May 2003, Stephen Sprunk wrote:
Thus spake "Dan Hollis" <goemon@anime.net>
On Thu, 29 May 2003, Jack Bates wrote:
Dan Hollis wrote:
ok, what UPSes do telcos use (besides their monster battery arrays) What's wrong with our monster battery arrays? They dont tend to fit in 19" rackmounts You wouldn't mount a "monster array" in 19" racks anyways.
Yes, I was specifically asking what telcos use when they dont use the battery arrays.
they use smaller battery arrays... There's a pile of fujitsu tdm gear with four deep-cycle batteries in the basement of our facilty belong to quest...
Eg what do they use in remote cabinets or customer premise sites...
I thought it was a simple question, guess not.
-Dan
-- -------------------------------------------------------------------------- Joel Jaeggli Academic User Services joelja@darkwing.uoregon.edu -- PGP Key Fingerprint: 1DE9 8FCA 51FB 4195 B42A 9C32 A30D 121E -- In Dr. Johnson's famous dictionary patriotism is defined as the last resort of the scoundrel. With all due respect to an enlightened but inferior lexicographer I beg to submit that it is the first. -- Ambrose Bierce, "The Devil's Dictionary"
On Fri, 30 May 2003, Joel Jaeggli wrote:
Yes, I was specifically asking what telcos use when they dont use the battery arrays.
On Fri, 30 May 2003, Dan Hollis wrote: they use smaller battery arrays... There's a pile of fujitsu tdm gear with four deep-cycle batteries in the basement of our facilty belong to quest...
Well I did some checking off-list and this is what qwest uses at customer premise sites: http://www.marconi.com/html/about/mz5a50photos.htm -Dan -- [-] Omae no subete no kichi wa ore no mono da. [-]
On Thu, 29 May 2003, Stephen Sprunk wrote:
Thus spake "Dan Hollis" <goemon@anime.net>
On Thu, 29 May 2003, Jack Bates wrote:
Dan Hollis wrote:
ok, what UPSes do telcos use (besides their monster battery arrays) What's wrong with our monster battery arrays? They dont tend to fit in 19" rackmounts You wouldn't mount a "monster array" in 19" racks anyways. Yes, I was specifically asking what telcos use when they dont use the battery arrays. Eg what do they use in remote cabinets or customer premise sites... I thought it was a simple question, guess not.
for most sites I've seen, the 19" rack is too small for the monster array. they tend to use 23" racks and place the batts at the bottom - generally 3-6 hour runtime. --bill
bmanning@karoshi.com wrote:
for most sites I've seen, the 19" rack is too small for the monster array. they tend to use 23" racks and place the batts at the bottom - generally 3-6 hour runtime.
Yeah. A lot of the remote hardened equipment runs off small battery arrays as well. During major power outages, look for the poor sucker stuck with driving the circuit to keep them all charged. -Jack
Speaking on Deep Background, the Press Secretary whispered:
On Thu, 29 May 2003, Sean Donelan wrote:
The most annoying thing about UPSes is they fail at exactly the time they are needed most.
....Like tape drives..
ok, what UPSes do telcos use (besides their monster battery arrays)
-Dan
They eschew same. Telco stuph runs on that -48v. It's their steak & potato...err E. But the price is high and not just the cost. A telco string stores enough to qualify as weapons of mis destruction. Drop a wrench and learn Braille. You need a PE with a track record in battery plant design. You need a separate room, separate ventilation, separate entrance, etc. But your MTBF is many years. Yes, you lose individual loads, but the string carries on. Provided, of course, you keep the rectifiers running, and know when they fail...and fix same. (ATT NYC Toll switch and DACS...) -- A host is a host from coast to coast.................wb8foz@nrk.com & no one will talk to a host that's close........[v].(301) 56-LINUX Unless the host (that isn't close).........................pob 1433 is busy, hung or dead....................................20915-1433
participants (21)
-
Alex Rubenstein
-
Arman
-
Bill Woodcock
-
bmanning@karoshi.com
-
Dan Armstrong
-
Dan Hollis
-
David Lesher
-
David Raistrick
-
E.B. Dreger
-
Gerald
-
Jack Bates
-
Joel Jaeggli
-
Lars Erik Gullerud
-
listuser@numbnuts.net
-
nicholas harteau
-
Pete Ehlke
-
Robert Boyle
-
Sean Donelan
-
Simon Lockhart
-
Stephen Sprunk
-
Timothy Brown