Re: Why do we use facilities with EPO's?
A friend of mine is a volunteer firefighter (and ex-ISP CEO, used to be on the list). I'm not sure that he'd voluntarily enter a burning datacenter to put it out if there wasn't an EPO. Firefighters won't use water on live electrical fires. If your response plan to a fire in the datacenter is "the building burns down and hope nobody's inside it still" then you're set. I've seen someone electrocuted and frozen on the wire in a non-datacenter setting; we flipped the building breaker, which was further than an EPO would have been. It wasn't through his chest, and was only 110 V, so it probably didn't make a difference that it took a minute to turn it off instead of 10 seconds. There were no severe burns, etc. I've seen equipment catch on fire in a datacenter. If I hadn't been able to cut off the power locally, the EPO was the last line of defense... People I know have hit the EPO when sprinklers discharged in the datacenter. If you're lucky these won't happen to you. But that's not why safety rules are put in place. Unluck happens. -george william herbert gherbert@retro.com