All, We had an issue with a DC where temps were elevated. The one bit of hardware that wasn't watched much was the one that sent out the initial alert. Looking for recommendations on hardware that I can mount/hang in each cabinet that is easy to set up and will alert us if temps go beyond a certain point. TIA. Dovid
Yo Dovid! On Thu, 13 Jul 2017 22:33:22 -0400 Dovid Bender <dovid@telecurve.com> wrote:
Looking for recommendations on hardware that I can mount/hang in each cabinet that is easy to set up and will alert us if temps go beyond a certain point.
I use a lot of TEMPer USB Thermometers. Cheap, small, easy to poll. It is easy to use from many programing languages and lots of open source software supports it dierctly or indirectly. RGDS GARY --------------------------------------------------------------------------- Gary E. Miller Rellim 109 NW Wilmington Ave., Suite E, Bend, OR 97703 gem@rellim.com Tel:+1 541 382 8588 Veritas liberabit vos. -- Quid est veritas? "If you can’t measure it, you can’t improve it." - Lord Kelvin
On Thu, Jul 13, 2017 at 9:33 PM, Dovid Bender <dovid@telecurve.com> wrote:
All,
We had an issue with a DC where temps were elevated. The one bit of hardware that wasn't watched much was the one that sent out the initial alert. Looking for recommendations on hardware that I can mount/hang in each cabinet that is easy to set up and will alert us if temps go beyond a certain point.
TIA.
Dovid
Most everything has temperature sensors from switches, servers and most modern PDUs. A dedicated solution is just creating the problem again in the future. Monitor the temps on everything and gain knowledge related to failure rates. Most companies with physical infrastructure could pay for another engineer to discover these unexpected expenses. Also note that modern air conditioning and refrigeration have SNMP or BACNET protocol support, just download the manual. -- - Andrew "lathama" Latham -
Agreed -- there are already tons of temp sensors throughout old and new hardware. I've used SCSI drive queries via sdparm and more recently hddtemp to get the current temperature of the drives. No need for SNMP or ILO, though that can give you a more detailed picture where possible. You first monitor and record for 24 hours to get your baseline temp for a given rack or server, then set your threshold, then let your monitoring platform do the rest. Since I use hosted dedicated servers, I don't want to pay for yet another device. In monitoring only those disk temps I've caught two cooling issues before they became a crisis, one of which my hosting provider was not aware of. If you control the hardware, or at least have access to it, there should be enough sensors to let you know at least something is causing a problem. Beckman On Thu, 13 Jul 2017, Andrew Latham wrote:
On Thu, Jul 13, 2017 at 9:33 PM, Dovid Bender <dovid@telecurve.com> wrote:
All,
We had an issue with a DC where temps were elevated. The one bit of hardware that wasn't watched much was the one that sent out the initial alert. Looking for recommendations on hardware that I can mount/hang in each cabinet that is easy to set up and will alert us if temps go beyond a certain point.
TIA.
Dovid
Most everything has temperature sensors from switches, servers and most modern PDUs. A dedicated solution is just creating the problem again in the future. Monitor the temps on everything and gain knowledge related to failure rates. Most companies with physical infrastructure could pay for another engineer to discover these unexpected expenses. Also note that modern air conditioning and refrigeration have SNMP or BACNET protocol support, just download the manual.
-- - Andrew "lathama" Latham -
--------------------------------------------------------------------------- Peter Beckman Internet Guy beckman@angryox.com http://www.angryox.com/ ---------------------------------------------------------------------------
On 7/13/17 7:33 PM, Dovid Bender wrote:
All,
We had an issue with a DC where temps were elevated. The one bit of hardware that wasn't watched much was the one that sent out the initial alert. Looking for recommendations on hardware that I can mount/hang in each cabinet that is easy to set up and will alert us if temps go beyond a certain point.
TIA.
Dovid
Are you running ntpd on your boxes? See what happens when you plot its drift against other temperature sensors, the closer to the clock chip the better. If you do this on enough boxes, you should have an easy time seeing what happens on boxes where you have an easier time watching ntpd's drift value than you have watching a nearby dedicated temperature sensor. -- Harlan Stenn <stenn@nwtime.org> http://networktimefoundation.org - be a member!
Harlan Stenn wrote:
If you do this on enough boxes, you should have an easy time seeing what happens on boxes where you have an easier time watching ntpd's drift value than you have watching a nearby dedicated temperature sensor.
sweet from a technical point of view, but if you have elevated temperatures in a DC (happens all the time with CRACs tripping out), and you need to report this to the DC operations centre and the conversation would be hilarious if you started talking about ntpd drift customer: ohai, we're seeing the sort of clock drift from ntp monitoring that suggests there is a temperature issue near cabinet X. datacentre: huh, what's ntp? customer: it's a time control protocol. datacentre: the time is 12:23. Closing the ticket now. customer: but you have a temperature problem! Our clocks said so! datacentre: ticket is closed. please open a new ticket. Repeat until customer gives up in despair. Three weeks later, the customer is billed for 14 smart hands tickets relating to asking what the time was. Nick
We have Sensaphones (sensaphone.com) in remote offices. We use IMS-4000s. They are a 1RU box with RJ45 jacks on the front. You can run CAT-5 to where you want to monitor something, and stick a module on the end of the cable. They have temp, humidity, generic NO/NC sensors, power sensors to graph voltage and alert on voltage swings etc. They can send emails, SNMP traps, or dial out with a modem. They also have a built in mic that can alert on noise increases. Some models allow you to dial in and listen to the room. On July 13, 2017 10:33:22 PM EDT, Dovid Bender <dovid@telecurve.com> wrote:
All,
We had an issue with a DC where temps were elevated. The one bit of hardware that wasn't watched much was the one that sent out the initial alert. Looking for recommendations on hardware that I can mount/hang in each cabinet that is easy to set up and will alert us if temps go beyond a certain point.
TIA.
Dovid
Weathergoose by IT watchdogs. 1U rackmount devices with very shallow depth of about an inch or two. Sensors are cheap, varied, and you can daisychain dozens of them together. So one server box can monitor entire row of racks. Loads of other features too for notification, escalation, and SNMP manageable. -mel via cell
On Jul 13, 2017, at 9:27 PM, Pete Baldwin <pete@tccmail.ca> wrote:
We have Sensaphones (sensaphone.com) in remote offices. We use IMS-4000s. They are a 1RU box with RJ45 jacks on the front. You can run CAT-5 to where you want to monitor something, and stick a module on the end of the cable. They have temp, humidity, generic NO/NC sensors, power sensors to graph voltage and alert on voltage swings etc. They can send emails, SNMP traps, or dial out with a modem. They also have a built in mic that can alert on noise increases. Some models allow you to dial in and listen to the room.
On July 13, 2017 10:33:22 PM EDT, Dovid Bender <dovid@telecurve.com> wrote: All,
We had an issue with a DC where temps were elevated. The one bit of hardware that wasn't watched much was the one that sent out the initial alert. Looking for recommendations on hardware that I can mount/hang in each cabinet that is easy to set up and will alert us if temps go beyond a certain point.
TIA.
Dovid
http://tyconsystems.com/index.php/products/tycon-power/tpdin-monitor-web/751... Is what I use in my cabinets. Has two temp sensors, one internal and one external. I put the external near the AC cold air output so I can get a diff and know if the AC is on. SNMP cacti graphs them nicely. I use one of the voltage sensors to monitor the cabinet doors via reed switches. In remote mountain sites also use for battery/solar voltages and to monitor wall warts for Utility power loss. /rh On Thu, Jul 13, 2017 at 7:33 PM, Dovid Bender <dovid@telecurve.com> wrote:
All,
We had an issue with a DC where temps were elevated. The one bit of hardware that wasn't watched much was the one that sent out the initial alert. Looking for recommendations on hardware that I can mount/hang in each cabinet that is easy to set up and will alert us if temps go beyond a certain point.
TIA.
Dovid
If all that you require is temperature monitoring, I recommend going through the SNMP MIBs and doing an snmpwalk of your devices to identify the sensors at the air intake... Unfortunately there are some devices which do not have air intake sensors, but only a sensor somewhere generally in the center of the motherboard. But other devices have temperature diodes nearly everywhere. The attached chart example from an Arista 1U switch is a device which is really good about identifying the location of the individual sensors in the MIB. When purchasing a temperature monitoring standalone device, I highly recommend something that is capable of not only temperature sensors but also highly useful things like relay controls, wire contacts for other equipment alarms, contacts for things like door/cabinet opening sensors, etc. With the right high-frequency snmp polling and trap setup you can use such a thing for a great deal more than just temperature. I have seen examples of the Tinycontrol v3 used by NOCs to grant third parties access to POPs via remotely triggered relays and magnetic strike door locks. Here's a couple of good examples: http://tinycontrol.pl/en/lan-controller/ http://tinycontrol.pl/en/accessories-lk-3-sensor/ http://www.controlbyweb.com/x332/ On Thu, Jul 13, 2017 at 10:45 PM, Richard Holbo <holbor@sonss.net> wrote:
http://tyconsystems.com/index.php/products/tycon-power/ tpdin-monitor-web/751-tpdin-monitor-web2
Is what I use in my cabinets. Has two temp sensors, one internal and one external. I put the external near the AC cold air output so I can get a diff and know if the AC is on. SNMP cacti graphs them nicely. I use one of the voltage sensors to monitor the cabinet doors via reed switches. In remote mountain sites also use for battery/solar voltages and to monitor wall warts for Utility power loss.
/rh
On Thu, Jul 13, 2017 at 7:33 PM, Dovid Bender <dovid@telecurve.com> wrote:
All,
We had an issue with a DC where temps were elevated. The one bit of hardware that wasn't watched much was the one that sent out the initial alert. Looking for recommendations on hardware that I can mount/hang in each cabinet that is easy to set up and will alert us if temps go beyond a certain point.
TIA.
Dovid
If all that you require is temperature monitoring, I recommend going through the SNMP MIBs and doing an snmpwalk of your devices to identify the sensors at the air intake... Unfortunately there are some devices which do not have air intake sensors, but only a sensor somewhere generally in the center of the motherboard. But other devices have temperature diodes nearly everywhere. This chart example from an Arista 1U switch is a device which is really good about identifying the location of the individual sensors in the MIB. http://imgur.com/a/4CfpK When purchasing a temperature monitoring standalone device, I highly recommend something that is capable of not only temperature sensors but also highly useful things like relay controls, wire contacts for other equipment alarms, contacts for things like door/cabinet opening sensors, etc. With the right high-frequency snmp polling and trap setup you can use such a thing for a great deal more than just temperature. I have seen examples of the Tinycontrol v3 used by NOCs to grant third parties access to POPs via remotely triggered relays and magnetic strike door locks. Here's a couple of good examples: http://tinycontrol.pl/en/lan-controller/ http://tinycontrol.pl/en/accessories-lk-3-sensor/ http://www.controlbyweb.com/x332/ On Thu, Jul 13, 2017 at 10:45 PM, Richard Holbo <holbor@sonss.net> wrote:
http://tyconsystems.com/index.php/products/tycon-power/ tpdin-monitor-web/751-tpdin-monitor-web2
Is what I use in my cabinets. Has two temp sensors, one internal and one external. I put the external near the AC cold air output so I can get a diff and know if the AC is on. SNMP cacti graphs them nicely. I use one of the voltage sensors to monitor the cabinet doors via reed switches. In remote mountain sites also use for battery/solar voltages and to monitor wall warts for Utility power loss.
/rh
On Thu, Jul 13, 2017 at 7:33 PM, Dovid Bender <dovid@telecurve.com> wrote:
All,
We had an issue with a DC where temps were elevated. The one bit of hardware that wasn't watched much was the one that sent out the initial alert. Looking for recommendations on hardware that I can mount/hang in each cabinet that is easy to set up and will alert us if temps go beyond a certain point.
TIA.
Dovid
We use Asentria. On 07/13/17 22:33 -0400, Dovid Bender wrote:
All,
We had an issue with a DC where temps were elevated. The one bit of hardware that wasn't watched much was the one that sent out the initial alert. Looking for recommendations on hardware that I can mount/hang in each cabinet that is easy to set up and will alert us if temps go beyond a certain point.
-- Dan White BTC Broadband Network Admin Lead Ph 918.366.0248 (direct) main: (918)366-8000 Fax 918.366.6610 email: dwhite@olp.net http://www.btcbroadband.com
we use: https://serverscheck.com/sensors/ - simple setup, graph nicely in Cacti. I went with ServerCheck wired based units + external temp+humidity probe. The base unit displays the temperature which is a nice quick reference if you are in the room. On Fri, Jul 14, 2017 at 8:31 AM, Dan White <dwhite@olp.net> wrote:
We use Asentria.
On 07/13/17 22:33 -0400, Dovid Bender wrote:
All,
We had an issue with a DC where temps were elevated. The one bit of hardware that wasn't watched much was the one that sent out the initial alert. Looking for recommendations on hardware that I can mount/hang in each cabinet that is easy to set up and will alert us if temps go beyond a certain point.
-- Dan White BTC Broadband Network Admin Lead Ph 918.366.0248 (direct) main: (918)366-8000 Fax 918.366.6610 email: dwhite@olp.net http://www.btcbroadband.com
+1 for the serverscheck.com gear. Been running it as a humidity monitor in the plant for a year or so now and it's been rock solid. If you're the kind of shop that requires calibration for that sort of equipment they'll handle that as well. Great company to work with. Pair it with Cacti + thold plugin or whatever other snmp monitoring you like - or the base units can handle alerting on their own. FYI for those interested - the stated max length of connecting cable between the base station and the sensor units (30ft iirc) is way under what it'll do in the real world - I've got at least one sensor unit that's a good 500ft away from the base station and it's been working just fine Ed Pers -----Original Message----- From: NANOG [mailto:nanog-bounces@nanog.org] On Behalf Of David Charlebois Sent: Sunday, July 16, 2017 10:02 PM To: NANOG <nanog@nanog.org> Subject: Re: Temperature monitoring we use: https://serverscheck.com/sensors/ - simple setup, graph nicely in Cacti. I went with ServerCheck wired based units + external temp+humidity probe. The base unit displays the temperature which is a nice quick reference if you are in the room. On Fri, Jul 14, 2017 at 8:31 AM, Dan White <dwhite@olp.net> wrote:
We use Asentria.
On 07/13/17 22:33 -0400, Dovid Bender wrote:
All,
We had an issue with a DC where temps were elevated. The one bit of hardware that wasn't watched much was the one that sent out the initial alert. Looking for recommendations on hardware that I can mount/hang in each cabinet that is easy to set up and will alert us if temps go beyond a certain point.
-- Dan White BTC Broadband Network Admin Lead Ph 918.366.0248 (direct) main: (918)366-8000 Fax 918.366.6610 email: dwhite@olp.net http://www.btcbroadband.com
Would be pretty great if mobile worked... 😎 -- Onward!, Jason Hellenthal, Systems & Network Admin, Mobile: 0x9CA0BD58, JJH48-ARIN On Jul 18, 2017, at 15:39, Edwin Pers <EPers@ansencorp.com> wrote: +1 for the serverscheck.com gear. Been running it as a humidity monitor in the plant for a year or so now and it's been rock solid. If you're the kind of shop that requires calibration for that sort of equipment they'll handle that as well. Great company to work with. Pair it with Cacti + thold plugin or whatever other snmp monitoring you like - or the base units can handle alerting on their own. FYI for those interested - the stated max length of connecting cable between the base station and the sensor units (30ft iirc) is way under what it'll do in the real world - I've got at least one sensor unit that's a good 500ft away from the base station and it's been working just fine Ed Pers -----Original Message----- From: NANOG [mailto:nanog-bounces@nanog.org] On Behalf Of David Charlebois Sent: Sunday, July 16, 2017 10:02 PM To: NANOG <nanog@nanog.org> Subject: Re: Temperature monitoring we use: https://serverscheck.com/sensors/ - simple setup, graph nicely in Cacti. I went with ServerCheck wired based units + external temp+humidity probe. The base unit displays the temperature which is a nice quick reference if you are in the room.
On Fri, Jul 14, 2017 at 8:31 AM, Dan White <dwhite@olp.net> wrote:
We use Asentria.
On 07/13/17 22:33 -0400, Dovid Bender wrote:
All,
We had an issue with a DC where temps were elevated. The one bit of hardware that wasn't watched much was the one that sent out the initial alert. Looking for recommendations on hardware that I can mount/hang in each cabinet that is easy to set up and will alert us if temps go beyond a certain point.
-- Dan White BTC Broadband Network Admin Lead Ph 918.366.0248 (direct) main: (918)366-8000 Fax 918.366.6610 email: dwhite@olp.net http://www.btcbroadband.com