I have had to do this at times but it is not strictly allowed by codes and not at all recommended.
It's an active fire hazard. The cables aren't rated (= built) for the power draw.
Meh. It depends. Plug that 30 amp power strip into a 20 amp circuit. Try to use more than 20 amps and the main breaker trips. No problem. Plug that 20 amp power strip into a 30 amp circuit. Try to use more than 20 amps and the strip's breaker trips. No problem. Get a short before the strip breaker and the main breaker trips before the wires can heat. There just aren't a whole lot of failure modes here that result in fire short of one or the other breaker failing. And that results in fire regardless of the amperage mismatch. This, by the way, is why you're allowed to plug that 22 gauge Christmas light wire into a 15 amp receptacle even though it can't handle 15 amps: the 3 amp fuse will blow if there's a short. Just don't plug in anything with lower-rated wire that doesn't have its own breaker or fuse. Regards, Bill Herrin -- William D. Herrin ................ herrin@dirtside.com bill@herrin.us 3005 Crane Dr. ...................... Web: <http://bill.herrin.us/> Falls Church, VA 22042-3004