On Mon, 14 Nov 2011, Sam (Walter) Gailey wrote:
My question is this; Is there an appropriate standard to specify for fiber-optic cabling that if it is followed the fiber will be installed correctly? Would specifying TIA/EIA 568-C.3, for example, be correct?
I'm envisioning something like;
"The vendor will provide fiber connectivity between (building A) and (building B). Vendor will be responsible for all building penetrations and terminations. When installing the fiber-optic cable the vendor will follow the appropriate TIA/EIA 568 standards for fiber-optic cabling."
How you phrase the requirements depends on what you want the end result to be. Sorry to start this off with a wishy-washy statement, but when dealing with contractors, you have to be very specific with what you want, and stay involved during the project, to be sure the results are what you want. It's a good idea to define very clearly what is "in scope" and "out of scope" for the contractor up front. This can include things like the contractor being responsible for submitting any one-call requests per your localities' guidelines for any work that requires digging, or restoring any items that have to be removed (landscaping, sidewalks, paved roadways, etc) to facilitate digging. For example, do the buildings in question already have usable entrance facilities for communications (aerial/underground entrances, suitable demarc locations in each building, cable pathways from the exterior penetrations to the demarc point)? If not, you will generally need to spell out exactly what the fiber contractor (or a sub-contractor) is expected to provide (conduits from comms manhole/utility vault/pole/etc). Typically you will need to define a place in each building where the fiber will land, which will either be in a rack or on a wall. Also, at a minimum, the contractor should 1. test all strands at the appropriate wavelengths, 2. provide you with documentation of the test results, and 3. general fit-and-finish/workmanship items such as making sure all connectors have dust caps and any required labeling of the termination bays. Where I work, we have detailed construction / installation standards that get added to the bid package of any new construction or major renovation on our campus. If you want, I can send you a copy (off-list) of the relevant pieces of our Division 27 specs that go out to contractors as part of our construction bid packages. jms