We considered this approach, but we wanted to have notifications precede shut down, and give a remote support person the ability to prevent the shut down. Our SNMP based system gives us that option. -mel
On May 27, 2019, at 11:16 AM, Brian Kantor <Brian@ampr.org> wrote:
A simple air conditioner thermostat wired to the EPO switch. For safety, wire two thermostats in series so BOTH have to trip before power is shut off.
Note that the EPO rarely does an orderly shutdown, but then this is a sort of an emergency. - Brian
On Mon, May 27, 2019 at 02:00:39PM -0400, Dovid Bender wrote: Hi,
Is anyone aware of a device that will cut the power if the room goes above X degrees? I am looking for something as a just in case.