SmartJack with demarcation point in the office (or same floor) instead of the building entrance point
I can't emphasize enough the importance of this, read ahead.
Mark Kent wrote: You are not likely going to be able to control that, it depends on how the install tech's day is going. Strictly speaking, I believe they are supposed to put it at the MPOE.
For the smart jack, it depends on the telco and/or if the telco also is the CLEC. Example1: You buy the T1 from AT&T, and they use SBC (formerly Pacific Bell) as the CLEC. The only way you will get the demarc extended in your premises is to have the router managed by AT&T, and then the demarc is the Ethernet port of their router. If you have your own router the demarc is the smart jack, the smart jack is at the MPOE and anything between the smart jack and you is your responsibility, which is terrible as I will explain below. Example2: You buy the circuit from XO and they are their own CLEC. As you hold the sales droid by the cojones you will be able to have the demarc extended to your premises.
As you order the circuit specify where you want it to end up ("server room, 2nd floor") and that you want an extended demarc (will cost extra).
Yes, yes, yes. It is worth the extra cost.
AT install time, make sure someone is around to cajole the installer into getting the NIU as close as you can to where your router will be.
This is where there isn't much you can do about. I have tried several times to "cajole" with 200 bucks in cash and/or other incentives; it did not happen.
The installer should test from the extended demarc (make sure they do).
The installer and all the techs always test from the demarc, whether or not it's extended. What you DON'T want to do is to extend the demarc yourself (because you don't actually extend it), and here's why: - Let's assume example 1 above. - The demarc is at the MPOE; the smart jack is 1ft away from the NIU; you have a 300ft cat5 cable between the smart jack and the CSU/DSU in your premises. - You drop packets; you have 65 identically configured sites, you replaced the router and the CSU/DSU twice already, and you still drop packets. As the config can't be at fault as it works fine on the other 64 sites and the hardware can't be at fault since you replaced every piece of it including the power cord and the patch cords twice, it's obviously a circuit issue, right? - You call AT&T. "It works on my side" (remember this sentence). - You call SBC. "It works on my side". That is, if you get them to talk to you as the circuit goes to AT&T and they will likely say "talk to them". - You call AT&T again. "It works on my side". - You call your AT&T sales droid and threaten not to pay the bill and sue them. - After 2 days of ping-pong you finally get an SBC tech to come and test the line (possibly by lying at the number of CRC errors). - The SBC tech comes, plugs the pattern tester at the smart jack, loops the remote CSU/DSU, and it all tests clean. - The SBC tech report that the circuit is clean, now you're back dealing with AT&T. - More time passes by. You finally get the AT&T tech to come. He does the same as the SBC tech: plugs the tester at the demarc and runs bit patterns. "It works on my side". - You say: but I need it to work at my router, not in the MPOE room. Tough luck, buddy. Our responsibility stops at the demarc; it tests clean, we don't give a rip if you extended the demarc to your office. Tough luck. Sometimes pattern testers detect line issues, sometimes they don't. Now you have to move your CSU/DSU and router in the MPOE room (possibly open to all winds) and _prove_ them that it's a circuit issue. Morale: you want the demarc extended to the same room you have the CSU/DSU in your premises, ESPECIALLY if there is more than one company involved.
Get a standard built-in T1 dsu like as been mentioned in previous posts. Plug it into the extended demarc with an ethernet patch cable.
Yes indeed. CAT5 is your friend even if it's not necessary on paper. Michel.