It ismy understanding also that most commercial grade gensets have built into the ATS logic that when utility power comesback online, that the transfer back to utility power is coordinated with the ATS driving the generator until both frequency and phases are within a user specified range? - mike On Jun 25, 2011, at 3:12 PM, Leo Bicknell <bicknell@ufp.org> wrote:
In a message written on Fri, Jun 24, 2011 at 06:29:14PM -0400, Jay Ashworth wrote:
I believe the answer to that question is contained here:
http://yarchive.net/car/rv/generator_synchronization.html [1]
I wouldn't use a colo that had to sync their generator to the grid. That is a bad design.
Critical load should be on a battery or flywheel system. When the utility is bad (including out) the load should be on the battery or flywheel for 5-15 seconds before the generators start. The generators need to sync to each other.
Essential load (think lighting, AC units) get dropped completely for 30-60 seconds until the generators are stable, and then that load gets hooked back in.
I have never seen a generator that syncs to the utility for live, no break transfer. I'm sure such a thing exists, but that sounds crazy dangerous to me. Generators sync to each other, not the utility.