Date: Sun, 12 Jan 2003 19:59:08 +0100 From: =?ISO-8859-1?Q?M=E5ns_Nilsson?= <mansaxel@sunet.se> Sender: owner-nanog@merit.edu
Some hours reading the back issues of the journal found at http://www.compliance-club.com will hopefully inform you why star grounding is a thing of the past. Ground both ends. If you are afraid of ground loops, place a heavy (as in 10-16mm2 or AWG way below 10) ground conductor alongside the signal cable, and ground it firmly in both ends. That will take the current away from the shields.
Ungrounded shileds are inefficient for EMI and RF shielding, while at times efficient AC hum blockers.
And, IANAEE, but I've played with big sound systems that exhibit all these problems.
I find this simply frightening! Have you any idea how much potential of ground can vary in a large building? It's easy to have AMPS of current flowing through the shield of a cable and enough voltage offset to be dangerous to people. (802.3 allows enough breakdown potential that the equipment is unlikely to have a problem, though.) Grounded at one end is better than floating for shielding, so this almost reasonable (as long as the wiring is all installed to spec) but grounding at both ends in the wrong environment can lead to serious problems. Since the 802.3 sections on 10Base-T does not deal with shielded wire at all, there is nothing there on the subject. But other sections on 10Base5 and 10Base2 are explicit that 10Base5 MUST be grounded at exactly one point and 10Base2 recommends that one point be grounded when the cable extends out of a room. More than one ground is explicitly prohibited. The archives of comp.dcom.lans.ethernet are full of people who have high error rates because of multiple grounds. R. Kevin Oberman, Network Engineer Energy Sciences Network (ESnet) Ernest O. Lawrence Berkeley National Laboratory (Berkeley Lab) E-mail: oberman@es.net Phone: +1 510 486-8634