I have a pure curiosity question for the NANOG crowd here. If you run your facility/datacenter/cage/rack on 120 volts, why?
We are using 120V in our colocation spaces.
I've been running my facility at 208 for years because I can get away with lower amperage circuits. I'm curious about the reasons for using high-amp 120 volt circuits to drive racks of equipment instead of low-amp 208 or 240 volt circuits.
The reason why we are using 120V is because we have pre-existing equipment (such as PDUs) that only support 120V operation. I believe our newer PDUs support 120/208/240, but do not have the time to investigate that, and we still have a couple of older APC units still in service. Our servers don't really care which voltage we provide, most of the PSUs can determine 120 vs 240 automatically, even. Also, at least at Equinix Chicago, 120V service was cheaper when we colocated there. I do not know if this is the same case at Steadfast in Chicago, and as far as I know, HE does not offer 208/240 service in their Fremont-2 facility. I could be misinformed on that, though. -- William Pitcock SystemInPlace - Simple Hosting Solutions 1-866-519-6149