{I'm no electrician, so this is all 'as I learned it'....} A) In the US, the breaker is rated to protect the outlet: 20A outlet, 20A breaker, etc. B) Each plug/jack set is unique; this stops you from accidently putting 250 on the 125 power supply. But it also stops you from using a 20A plug in a 30A receptacle... C) Big exception: you can use 5-15R aka 15 amp receptacles on 20A circuits. Further, the 5-20 receptacles accept either 5-15 or 5-20 plugs. -- A host is a host from coast to coast.................wb8foz@nrk.com & no one will talk to a host that's close........[v].(301) 56-LINUX Unless the host (that isn't close).........................pob 1433 is busy, hung or dead....................................20915-1433