On 6/25/2011 16:43, Paul Graydon wrote:
On 6/25/2011 12:32 PM, Seth Mattinen wrote:
For open and closed transitions you'll most certainly want to sync to utility to transition between the two. For the delayed transition model it'll stop at the intermediate "open" point for a configurable amount of time during which the load is disconnected from everything (i.e. let all the motors spin down first).
~Seth
Take a guess what the datacenter our equipment is currently hosted in uses. Yet another reason to be glad of a datacenter move that's coming up.
Also depends on the operator, so ask to see their xfer switches and how they're programmed if that's a concern. All of the non-residential models in that link for three-phase have motor/load disconnect signaling capability. If the operator is clued enough to use it then it's all good: shut off signal to motor/compressor loads, phase sync and switch, signal reconnect after delay. But if they're not... run away. Even with the delayed transition models the "hold open" delay can be too short and end up re-energizing the motors too quickly. There's always plenty of ways to f*ck things up good. ~Seth