http://www.amazon.com/Conntek-Locking-Adapter-Straight-Connector/dp/B001H9TS... If you're not sure, then spend for an hour with a licensed electrician. -- Joe Hamelin, W7COM, Tulalip, WA, 360-474-7474 On Fri, Aug 16, 2013 at 2:47 PM, Nick Khamis <symack@gmail.com> wrote:
Hello Everyone,
We are in the market for a APC UPS, and had a few questions. We are not that familiar with APC, and was hoping for some clarity. Our power demands will be for a unit that will sustain 3 kW/4 kVA scalable to 8 kVA.
Input:
The first issue is that I see all the units default with 208v input (other inputs 240v). At my location we only have 120 or 240. Also, we do not want to use a transformer (240-120) as it adds another failure point that can be avoided...
The unit we are looking is found here:
http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SYA4K8RMP&total_watts=500
Output:
Hard Wire 4-wire (2PH + N +G)NEMA L14-30R[image: NEMA L14-30R]NEMA L5-20R[image: NEMA L5-20R]
What? How do I plug our 120 PDU into this?
STONITH:
This will be for a cluster that will require stonith capability. Does anyone know if this unit supports that? Not so important as the previous two questions...
Kind Regards,
Nick.