On May 26, 2009, at 1:48 PM, Alex H. Ryu wrote:
Also, adding followings.
5) availability from local power provider(s)
I don't know of anywhere in the US/Canada where power comes into the building as strictly 110-120V. That is almost always delivered either as 1 leg of a 3-phase 208 service (most commercial/industrial deliveries) or as two hots (240V across the two hots) and a neutral (120V from either hot to neutral). Most datacenters are taking much higher voltage feeds from their utilities and most of the readily available step-down transformers and UPSs will produce 208 three-phase or 240V as described above. I am not an expert on power outside of the US, but, to the best of my knowledge, Japan's 100V/50Hz is one of the few other countries using less than 208V as their standard.
6) local regulation such as fire department safety rules...
I seriously question this one. Can you point to any examples?
7) for your own safety... (120V may not kill people, but 240V can do...)
It's relatively easy to kill someone with 12V, so, I don't see how 10x that is significantly less dangerous than 20x. Sticking your fingers in a light socket is going to hurt regardless of the voltage. Yes, 240V can hurt more and faster, but, at the end of the day, it's not significantly more likely to kill you than 110. Fortunately, most servers don't have light sockets in the high voltage portion of the server.
If you want better, why not just have everything to DC power ? Something like 48V...
There's a whole host of reasons, but, the biggest one boils down to cost... Cost of the larger wires, cost of the increased line losses, etc. Owen
Alex
Wayne E. Bouchard wrote:
1) Equipment used to not be dual voltage
2) For smaller scale, 120V UPS and distribution equipment is usually cheaper
3) 120V embedded itself into operations as a result.
4) We're all lazy and hate change.
On Tue, May 26, 2009 at 12:39:10PM -0700, Seth Mattinen wrote:
I have a pure curiosity question for the NANOG crowd here. If you run your facility/datacenter/cage/rack on 120 volts, why?
I've been running my facility at 208 for years because I can get away with lower amperage circuits. I'm curious about the reasons for using high-amp 120 volt circuits to drive racks of equipment instead of low-amp 208 or 240 volt circuits.
~Seth
--- Wayne Bouchard web@typo.org Network Dude http://www.typo.org/~web/